Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Reading Pump Curve 6

Status
Not open for further replies.

resilientsoma

Mechanical
Jul 11, 2012
34
0
0
SE
Hello all,
When looking at a pump curve, how do you determine if it's safe to run at a certain GPM without causing harm to the pump internals (seals, bearings, impeller).

For example, FLYGT 3300.181 : CLICK FOR SPECS

If I ran my system at 90 GPM, would this be okay and why (please feed me some basics)? If not, what can be the damage? Anything to recommend or change in the system besides picking a new pump?

Your help is greatly appreciated. I'm a new engineer; hopefully I'll be able to help someone later on!!!
 
Replies continue below

Recommended for you

I've found that a typical VFD and pump setup (not closed circuit piping) only works well between 75 to 85% of rated full speed BEP flowrate. Above 85% you should use a control valve, below that, either too low a head output, or power costs due to multiple inefficiency hits runs the bill up too high to make pumping for profit feasible. If you must have it for some reason, for very short-time flows, I guess you must, but don't try to pump those rates and make a living at it.

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek
 
@ Big Inch : Wow, what a wealth of knowledge; I truly appreciate your time.

I'm feeling stupid again: I can't seem to match my pump with your 4 highlighted points. The most kW I've seen was 71.8, 115.5 A, and 59.2 Hz. The kW in the PDF are much higher.

I am starting to wake up to reality to see a smaller pump would be much easier and more cost-effective.

I will try to change the RPM this week and re-measure. Have some other things to look into first.

Also, even with running low GPM out of the BEP range w/ VFD, you will still experience non-uniform radial thrust? Running a VFD lowers the efficiency, so you have to "pay to play." Pumps are more difficult than I thought.
 
On these straight line pump curves it's sometimes hard to tell. Estimate it at about where 75% to 85% of motor power rating is being consumed, estimating the efficiency of the pump at that point of around 75%. It might be a long shot, but it's the only shot you've got without the real curve.

"The kW in the PDF are much higher" I forget exactly, but I think starting currents can be maybe 2-4 times higher than run currents. EE is my weak suit.

Off-BEP ops with a VFD isn't the same problem for a pump varying flow while running at constant speed at a fixed BEP, as a lot of the forces and pressures retain balance as the BEP moves more closely with the change in flowrate. The problems encountered with VFDs manifest themselves on the power side.

In engineering, if you've really got a handle on what you are doing, you will always realize that trade-offs are being made and that the trade-offs come at a definate cost... somewhere. You've got to figure out where the penalties are being levied and how big they are. "No free lunches" and "You can't fool Mother Nature" are the reoccuring themes.

At 100% BEP, a control valve is probably fully open and no efficiency is lost there, but at 100% flow with the VFD on, you're paying maybe 5% eff loss just to have it there. That's why I say 85-100% BEP flow is better done with a control valve, as actual power losses are less than, or very close to, the VFD's 5% loss, - possible problems with power line harmonics and bearing corrosion. From 50% to 85% is VFD territory, provided you have available head when speed is lower (not for example as for Boiler Feed Water systems, etc. where head requirements remain high even for small flows, or for longer pipelines with + elevation changes). For a VFD to be economical, you have to spend some major percentage of pump time at 50-85% flowrates, which in that case may mean that you've set your system flowrate target too high and it probably should be lowered, making the control valve the more optimal solution once again. Lower than 50% BEP many system start to fall apart due to multiple efficiency reductions and not many systems work well at those flowrates at all, aside from cooling water closed circuits, etc. See my drift? A VFD on a submersible well pump is a real waste of money, as the high constant head required to reach the surface, even at low flows, will blow that idea. But I'm sure that somewhere they can be useful, I just don't often see too many of those cases in my pipeline work. If I need low to no flow, I'll pump to a tank at BEP flowrate, then shut the pipeline down until the tank starts getting low enough to pump full BEP flowrate into it again. That's he best way to save money. In any case, my usual objective is to pump as much as possible from point A to point B and actually neither a control valve or a VFD helps me out much there. I've generally lived a pretty long life without much use for them.

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek
 
Sorry for the delays! I understand the trade-offs, and VFD's aren't the most ideal scenario. I will take all of this into consideration for sure. We use the pumps for constant flow for process requirements, so it's either a smaller pump, or run w/ VFD and/or bypasses. A smaller pump to handle the low flow isn't favored due to not being able to have a back-up pump in the tank if one fails that is used for larger flows. A bypass can be created at the manifold, but will not be any cheaper unfortunately. Again, I appreciate all the insight and realize I have much to learn and experience. Thank you.
 
At least you are making a somewhat more "informed" decision.

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek
 
@ BigInch :

Yes sir, I'm trying. Thanks for your time and patience!

For an update: I'm working on nozzle selection, looking at PSI needed for area coverage. Next will be bypass constructions w/ PLC control. Fun stuff.
 
Have fun while it lasts.

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek
 

"resilientsoma (Mechanical)
..................... Pumps are more difficult than I thought."

You can't get anything much simpler than a centrifugal pump, it's all in the way you employ / install them.

You simple solution is to install a smaller pump dedicated to the 90 GPM application.

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
 
Status
Not open for further replies.
Back
Top