bookowski
Structural
- Aug 29, 2010
- 983
This should be an easy one that comes up a lot but I can't find a good answer.
How do you deal with rebar that has very low demand and also a very small embedment length. In my case I need to leaves dowels up for a cantilevered CMU wall on a slab on metal deck. The tension forces in the rebar will be small, about 1k unfactored, but the embedment depth is obviously limited.
ACI sets a minimum Ldh for hooks at 6in., this wouldn't be possible even if I was sure the bars would line up with a flute which most likely they won't. So that rules out calculating Ldh. It also doesn't seem reasonable to use the Asprovided/Asrequired provision on Ld to such an extreme degree.
Chapter D is only for anchors, they direct you elsewhere for pullout of rebar (at least that's how I'm reading it). Intuitively I can't imagine that 1k is going to pull out a #4 hooked 3 or 4 in. into a slab but it would be nice to be sure.
How do you deal with rebar that has very low demand and also a very small embedment length. In my case I need to leaves dowels up for a cantilevered CMU wall on a slab on metal deck. The tension forces in the rebar will be small, about 1k unfactored, but the embedment depth is obviously limited.
ACI sets a minimum Ldh for hooks at 6in., this wouldn't be possible even if I was sure the bars would line up with a flute which most likely they won't. So that rules out calculating Ldh. It also doesn't seem reasonable to use the Asprovided/Asrequired provision on Ld to such an extreme degree.
Chapter D is only for anchors, they direct you elsewhere for pullout of rebar (at least that's how I'm reading it). Intuitively I can't imagine that 1k is going to pull out a #4 hooked 3 or 4 in. into a slab but it would be nice to be sure.