Hi;
I have a 2-stage (tandem) reciprocating compressor train. Each stage has a recycle valve to control the suction pressure.
The compressor capacity is control by:
• Speed control (only by the 1st stage suction pressure)
• Clearance pocket
During the HAZOP of the project, it was requested to review requirement of the minimum recycle arrangement for the compressors to protect the train against a blocked compressor discharge. I have the following questions:
1) I think if a recycle line is required it should be designed for full compressor capacity. For a centrifugal compressor the minimum recycle is clear but what can be minimum recycle for a reciprocating compressor?
2) What is the advantage /disadvantage of an additional recycle line to protect the compressor against blocked discharge?
3) Can a separate transmitter be considered instead of recycle line to increase the protect level of the compressors against blocked discharge?
4) Can a discharge pressure control be added to the existing control valve to override the suction pressure control in case of high discharge pressure condition?
It should be noted:
• For blocked discharge protection each stage has one pressure transmitter for alarm/trip (common transmitter) and a PSV.
• The recycle valve maintains the suction pressure so in case of blocked discharge, the valve is closed as the suction pressure is increased (it is opened only in case of low suction pressure)
• The SIL level of the transmitter cannot meet the plant safety target so an additional layer of protection should be added to the system.
I have a 2-stage (tandem) reciprocating compressor train. Each stage has a recycle valve to control the suction pressure.
The compressor capacity is control by:
• Speed control (only by the 1st stage suction pressure)
• Clearance pocket
During the HAZOP of the project, it was requested to review requirement of the minimum recycle arrangement for the compressors to protect the train against a blocked compressor discharge. I have the following questions:
1) I think if a recycle line is required it should be designed for full compressor capacity. For a centrifugal compressor the minimum recycle is clear but what can be minimum recycle for a reciprocating compressor?
2) What is the advantage /disadvantage of an additional recycle line to protect the compressor against blocked discharge?
3) Can a separate transmitter be considered instead of recycle line to increase the protect level of the compressors against blocked discharge?
4) Can a discharge pressure control be added to the existing control valve to override the suction pressure control in case of high discharge pressure condition?
It should be noted:
• For blocked discharge protection each stage has one pressure transmitter for alarm/trip (common transmitter) and a PSV.
• The recycle valve maintains the suction pressure so in case of blocked discharge, the valve is closed as the suction pressure is increased (it is opened only in case of low suction pressure)
• The SIL level of the transmitter cannot meet the plant safety target so an additional layer of protection should be added to the system.