Reclosers

Status
Not open for further replies.

Markr

Electrical
May 3, 2000
6
I am looking at installing a recloser on diesel supplied distribution system. Can this be harmful to the diesel gensets to be opening an dclosing the line quick succession.


 
Replies continue below

Recommended for you

Off the top of my head, I would think you have to be careful about the load rejection and fast loading capabilities of the diesel genset. If it is a new recloser you can program whatever time you want for the reclose. This can then be coordinated with the genset limitations.
The genset will probably not have a problem with the load reject. Hopefully the system was spec to handle a complete load rejection. The real limitation is on how much load it can pickup rapidly.
 
If the reclose happens on to a fault, it could cause pole slip and thus stress the generator shaft.
 
Suggestion: It depends how the generator is loaded when the recloser call comes. Also, the genset control needs to be assessed for reclosing
 