sendinc
Mechanical
- Dec 24, 2023
- 4
Hello all, I recently started working in an area with high sensible and latent loads. I am trying to provide a solution for a previously installed system in a recently commissioned building where they are having condensation issues. The building was designed with FCUs to provide cooling for the room loads and four AHUs to provide 11% ventilation (100% OA, no return air at the AHU). The building was designed with a return plenum. The designers claim the problem is lack of filter maintenance causing negative pressure and infiltration. Our team thinks there is an issue with the design (and latent load calculation). The measured LAT at the AHU was 57F rather than designed 55F. I recently checked and the building is positively pressured with dirty filters.
My questions are:
-What are the most common designs to handle high latent loads? Does it sounds like the system is undersized (either chillers or AHUS) or is there a specific coil better suited to handle the latent load? Is it possible to install a different coil or something to provide precooling with the original coil and a reheat?
-Is it common to install a DOAS without a return duct? What are your thoughts on return plenums?
It appears they designed using for a sensible design day (114F DB/86F WB). I calculated the load using the 0.4% dehumidification day (93.3F DB/ 88F WB) and the total cooling load doesn't seem that different (2 tons more for latent design values for a 56,000 sqft building). However, if I draw a line between the latent design conditions and the actual measured LAT (57F, assume 90% RH), there is no ADP that would make this process physically possible. Am I missing something?
The load modeling completed from the designer was done in HAP for the FCUs only. They assumed an SHR of 0.9, but the modeling doesn't include any outdoor air. They calculated the cooling load for each individual room. I summed these values and came up with 196 tons. They installed two 113 ton air cooled chillers for a total capacity of 228 tons with a designed leaving chilled water temperature of 43F.
My questions are:
-What are the most common designs to handle high latent loads? Does it sounds like the system is undersized (either chillers or AHUS) or is there a specific coil better suited to handle the latent load? Is it possible to install a different coil or something to provide precooling with the original coil and a reheat?
-Is it common to install a DOAS without a return duct? What are your thoughts on return plenums?
It appears they designed using for a sensible design day (114F DB/86F WB). I calculated the load using the 0.4% dehumidification day (93.3F DB/ 88F WB) and the total cooling load doesn't seem that different (2 tons more for latent design values for a 56,000 sqft building). However, if I draw a line between the latent design conditions and the actual measured LAT (57F, assume 90% RH), there is no ADP that would make this process physically possible. Am I missing something?
The load modeling completed from the designer was done in HAP for the FCUs only. They assumed an SHR of 0.9, but the modeling doesn't include any outdoor air. They calculated the cooling load for each individual room. I summed these values and came up with 196 tons. They installed two 113 ton air cooled chillers for a total capacity of 228 tons with a designed leaving chilled water temperature of 43F.