adeschamps
Electrical
- Jul 11, 2013
- 2
Hello everyone.
We have a new 70MVA (34.5/1.0kV)transformer suppliying an EAF (Electric Arc Furnace). We took 2 oil samples within 4 days and I don't really understand the results:
GAS-----Feb-08-------Feb-12
H2-------3.79---------2.36
O2-------4,636--------2,492
N2-------14,704------8,123
CH4-------1.30--------0.75
CO--------4.41--------2.19
CO2-------83.05-------27.02
C2H4------0.13---------0.0
C2H6-------0.0--------0.13
C2H2-------0.19-------0.0
TGCD-------9.82-------5.43
None of the values is dangerous but I don't know how did the ammount of gases went down. We didn't do any degassing.
This got me thinking if the DGAs were perfomed correctly.
Is there any way a tranformer could lower it's dissolved gases by itself in such short time?
Thank you.