n39
Civil/Environmental
- Jan 16, 2023
- 38
Hi, I was developing a method to easily check for redundancy factor in my structure. I need some advice or input or correction if any of my understanding are wrong, and if I can use this method to check for redundancy. Thanks
"Loss of moment resistance at the beam-to-column connections at both ends of a single beam would not result in more than a 33% reduction in story strength; nor does the resulting system have an extreme torsional irregularity (horizontal structural irregularity Type 1b)"
Does this mean that:
1. I have to delete 1 beam member (randomly, just select one or perhaps it is better to select beam with the highest moment)
2. The sentences say that the deletion would not result in more than one a 33% reduction in story strength. Does this also mean that the structure must be able to withstand a 67% of the initial base shear?
3. To confirm my structure have pass this, I would apply 67% of the initial base shear and check all of the moment frame. If one of those fail, that simply means that my structure isn’t redundant and would have to use p=1.3. (I would use ETABS and use the concrete design check to see instantly whether the member are failing or not)
4. If all of my member passed the 67% of base shear, then I would have to check for extreme torsional irregularity
"Loss of moment resistance at the beam-to-column connections at both ends of a single beam would not result in more than a 33% reduction in story strength; nor does the resulting system have an extreme torsional irregularity (horizontal structural irregularity Type 1b)"
Does this mean that:
1. I have to delete 1 beam member (randomly, just select one or perhaps it is better to select beam with the highest moment)
2. The sentences say that the deletion would not result in more than one a 33% reduction in story strength. Does this also mean that the structure must be able to withstand a 67% of the initial base shear?
3. To confirm my structure have pass this, I would apply 67% of the initial base shear and check all of the moment frame. If one of those fail, that simply means that my structure isn’t redundant and would have to use p=1.3. (I would use ETABS and use the concrete design check to see instantly whether the member are failing or not)
4. If all of my member passed the 67% of base shear, then I would have to check for extreme torsional irregularity