I am working on a project that has Direct Expansion HVAC units installed to cool a birthing barge. The condenser units are on the roof and the AHU's are in the spaces throughout. We have been asked to go back a decide where refrigerant monitors should be located in the spaces below. Is there a specification or requirement for where to locate monitors and how to go about doing this? Since it is basically being used as a Hotel I can see the desire for leak detection for saftey reasons if you have a leak in a stateroom. Does anyone know if ASHRAE has any document to govern this type of design. Maybe something that bases the detection requirements off the size of the refrigerant charge?

Thanks
 
Replies continue below

Recommended for you

i use en 378 for that, while i believe it's ashrae 15 and/or 34
 
Right, Drazen -- ASHRAE 34 tells what (classification of refrigerants) and 15 tells how (where monitoring is required, how much refrigerant triggers it, how to arrange the ventilation and alarming, and other what-not).



Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
Thanks for the references, I will check them out.
 