Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Regarding deep beam design 2

Status
Not open for further replies.

Nayan67

Civil/Environmental
Feb 8, 2023
29
Hi all,
I am trying to design a capping beam that meets the definition of a deep beam, with an a/d ratio of around 1.0. I am curious about the standard practice for designing such a beam in terms of shear and flexure. Is it mandatory to design the beam using the strut and tie model? Alternatively, can we use equations available for ordinary beams to calculate the stirrups for shear force, and rely on beam theory for the computation of the flexural reinforcement?

Regards,
Nayan
 
Replies continue below

Recommended for you


If ( a) is span and a/d ratio of around 1.0, the beam is definitely deep beam. In this case , linear–elastic flexural theory and plane sections remaining plane after bending is no more valid and shear deformation dominates the behaviour.

You may design with STM modelling or follow the rules specified at your code .




Use it up, wear it out;
Make it do, or do without.

NEW ENGLAND MAXIM


 
Strut and tie seems to be the easiest approach.

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
for deep beams I used to use strut and tie method. I once used a second method that I found in the canadian concrete Handbook (Park & Paulay method) where you can use the regular equations (Mr, Vr,...) but with reducing d (leval arm) parameter (distance between rebar in tension and compressed fiber of concrete).I compared the results to the strut and tie method and the final design was similar. You can see the article from the book in the images below .
ParkPaulay_gtuhye.jpg
ParkPaulay2_qm5bvy.jpg
 
b = width of the wall?

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
Thank you so much everyone for your feedback.
 
thanks...

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
I guess this is a kind of grey area and STM itself is too liberal...
this topic is not clearly understood as a term 'disturbance' means.
For example, the above reference used distributed load; no difference for concentrated load condition?
Any data for pretension case like in the precast concrete walls? Just adjust compression strut and fy?
_JRW
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor