This is regarding a Rehab Project where the contractor is performing some work on the roof of a multi-story building.
The Contractor needs to install Scaffolding & Shoring for his work.
Typically what I have seen on Projects:
[ul]
[li]The Contractor's engineer is responsible for the load of the scaffolding on the Existing structure and for any damage or distress it so imposes.[/li]
[/ul]
[ul]
[li]The Contractor submits documents for EOR review and approval, including drawings indicating proposed Scaffolding & Shoring plan, relevant Calculations with a stamped letter from a registered engineer responsible for its preparation, acknowledging that the scaffolding does not overload the structure.[/li]
[/ul]
[ul]
[li]The Contractor is responsible for any engineering support required to accomplish his/her work.[/li]
[/ul]
I have drawn the below sketch to share the proposed plan submitted by the Contractor:
[ul]
[li]The submittal did not included a stamped letter or calculations by the Contractor's Engineer.[/li]
[/ul]
[ul]
[li]The contractor is supporting his Scaffolding & Shoring from existing suspended floor slabs and only provides reactions at these locations, with a note that " EOR shall check and approve the ability of the existing structure to safely support loads imposed by the scaffold.”[/li]
[/ul]
[ul]
[li]Since the Existing Building is in use during the rehab work, to avoid overloading the existing structure, I would generally expect the contractor to carry the shoring loads down to the soil/footing level by adding additional shores below the supporting floor (See markup in blue)[/li]
[/ul]
Looking for opinion on how this is typically handled on Building rehab projects.
[ul]
[li]Is EOR responsible for ability of the existing structure to safely support loads imposed by the scaffold? If so, how is the responsibility and legality handled. Since if the EOR does check the existing structure based on the support locations/loads provided by the contractor, what happens if the Contractor's loads are not correct (EOR does not know full details of how the loads were calculated) or the actual installation in field is different (EOR does not typically verify field installation of scaffolding and supports)[/li]
[/ul]
[ul]
[li]What if the existing structure cannot take the loads, the the scaffolding plan has to be revised. This needs a close coordination, back&forth between EOR and scaffolding engineer and Contractor. [/li]
[/ul]
[ul]
[li]EOR getting involved will lead to conflict of Interest problems (Contractor paying EOR for performing these calculations, while EOR is still employed by the Owner for overall work).[/li]
[/ul]
****** "TIL":You suddenly understand something you've understood all your life, but in a new way ~Doris Lessing ******
The Contractor needs to install Scaffolding & Shoring for his work.
Typically what I have seen on Projects:
[ul]
[li]The Contractor's engineer is responsible for the load of the scaffolding on the Existing structure and for any damage or distress it so imposes.[/li]
[/ul]
[ul]
[li]The Contractor submits documents for EOR review and approval, including drawings indicating proposed Scaffolding & Shoring plan, relevant Calculations with a stamped letter from a registered engineer responsible for its preparation, acknowledging that the scaffolding does not overload the structure.[/li]
[/ul]
[ul]
[li]The Contractor is responsible for any engineering support required to accomplish his/her work.[/li]
[/ul]
I have drawn the below sketch to share the proposed plan submitted by the Contractor:
[ul]
[li]The submittal did not included a stamped letter or calculations by the Contractor's Engineer.[/li]
[/ul]
[ul]
[li]The contractor is supporting his Scaffolding & Shoring from existing suspended floor slabs and only provides reactions at these locations, with a note that " EOR shall check and approve the ability of the existing structure to safely support loads imposed by the scaffold.”[/li]
[/ul]
[ul]
[li]Since the Existing Building is in use during the rehab work, to avoid overloading the existing structure, I would generally expect the contractor to carry the shoring loads down to the soil/footing level by adding additional shores below the supporting floor (See markup in blue)[/li]
[/ul]
Looking for opinion on how this is typically handled on Building rehab projects.
[ul]
[li]Is EOR responsible for ability of the existing structure to safely support loads imposed by the scaffold? If so, how is the responsibility and legality handled. Since if the EOR does check the existing structure based on the support locations/loads provided by the contractor, what happens if the Contractor's loads are not correct (EOR does not know full details of how the loads were calculated) or the actual installation in field is different (EOR does not typically verify field installation of scaffolding and supports)[/li]
[/ul]
[ul]
[li]What if the existing structure cannot take the loads, the the scaffolding plan has to be revised. This needs a close coordination, back&forth between EOR and scaffolding engineer and Contractor. [/li]
[/ul]
[ul]
[li]EOR getting involved will lead to conflict of Interest problems (Contractor paying EOR for performing these calculations, while EOR is still employed by the Owner for overall work).[/li]
[/ul]