ArsalanHabib
Mechanical
- Nov 3, 2012
- 4
Hi,
I usually use this forum when I don't understand anything and usually I find most of the answer through threads. I am trying to solve a problem here and I need some help. I am stuck with this problem I am sure any one in this forum can help me.
The problem is as follows.
Single Duct system with reheat serving two zones.
The thermostat setting is : 72degee F for heating & 78 degreeF for cooling.
Heating Load
Zone 1= 48000 btu/hr
Zone 2= 56000 btu/hr
Cooling Load
Zone 1=24000btuh
zone 2=50000btuh
For this system the supply air temp is 55degF all year round.
1.determine required zone air flow rates and capacity of AHU?
2. Calculate the reheat required for each zone and the temperature of the reheated air for each zone?
On a day at a certain time, the intermediate condition (off design) are given below
Heating Load
Zone 1= 24000 btu/hr
Cooling Load
zone 2=30000btuh
1. Without discriminator control, calculate the reheat required for each zone?
2. With discriminator control, calculate the reheat required for each zone and amount of saving?
I try yo solve it simply by Btus=1.09*CFM*deltaT but I am confused if I calculate the CFM through this using load BTUS and delta T by thermostat minus supply..... I don't understand am going to calculate amount of reheat and reheat temp. Please help I have a paper next week.
I usually use this forum when I don't understand anything and usually I find most of the answer through threads. I am trying to solve a problem here and I need some help. I am stuck with this problem I am sure any one in this forum can help me.
The problem is as follows.
Single Duct system with reheat serving two zones.
The thermostat setting is : 72degee F for heating & 78 degreeF for cooling.
Heating Load
Zone 1= 48000 btu/hr
Zone 2= 56000 btu/hr
Cooling Load
Zone 1=24000btuh
zone 2=50000btuh
For this system the supply air temp is 55degF all year round.
1.determine required zone air flow rates and capacity of AHU?
2. Calculate the reheat required for each zone and the temperature of the reheated air for each zone?
On a day at a certain time, the intermediate condition (off design) are given below
Heating Load
Zone 1= 24000 btu/hr
Cooling Load
zone 2=30000btuh
1. Without discriminator control, calculate the reheat required for each zone?
2. With discriminator control, calculate the reheat required for each zone and amount of saving?
I try yo solve it simply by Btus=1.09*CFM*deltaT but I am confused if I calculate the CFM through this using load BTUS and delta T by thermostat minus supply..... I don't understand am going to calculate amount of reheat and reheat temp. Please help I have a paper next week.