Reinf. Conc. Vault for Flowmeter

Status
Not open for further replies.

ChipperB

Civil/Environmental
Jul 7, 2004
33
0
0
US
I need to contruct a concrete vault over an active 30-in PVC C-900 wastewater force main. The flowmeter will be a strap on. My question concerns the pipe/wall penetrations. Because the walls will be poured around the existing force main is it ok for the new concrete to poured dircetly against the pipe or should I make arrangements for there to be some space between the new concrete and the pipe? If a spaace is required, what is a good technique for sealing around the pipe?

thanks
 
Replies continue below

Recommended for you

You should use a flexible rubber boot around the pipe. You should think about adding a sump pump since the meter may be ruined by ground water intrusion.
 
pre-cast doghouse is the way to go. you should be discussing this with your local pre-caster who can probably answer all your questions.
 