I have a situation i am not too sure on what to do. I have an existing non-reinforced Masonry wall that is insulated. The new roof is causing a bit of uplift on the wall(changed style and orientation) Thus i have to reinforce it. Originally, we specified to grout and reinforce the wall. Now we got word that it's insulated at every core, so the mason cannot make that work.
two options i thought about:
1. I was thinking to reinforce both sides with carbon fiber straps but thought about the weather exposer that might cause issues, also the client having issues with seeing straps on the outside every so often.
2. Reinforce both sides with steel channels, but the client is against having steel channels on the outside due to the "ugly" look.
Another option that i shot down was just reinforcing on the inside with steel channels, connecting every 16" from bottom to top. Spacing the channels every so often. I was against it, because it might help when wind blows against the wall, but not during "suction".
Another possible option i was thinking was to grout the top 2 or 3 cores down throughout the wall length to cancel out the uplift. It will make the wall top heavy, but if it works, why not?
Also, there are some vertical and diagonal cracks on the wall. This is kind of the main reason why i want to reinforce the wall.
what do you guys think?
Thanks!
two options i thought about:
1. I was thinking to reinforce both sides with carbon fiber straps but thought about the weather exposer that might cause issues, also the client having issues with seeing straps on the outside every so often.
2. Reinforce both sides with steel channels, but the client is against having steel channels on the outside due to the "ugly" look.
Another option that i shot down was just reinforcing on the inside with steel channels, connecting every 16" from bottom to top. Spacing the channels every so often. I was against it, because it might help when wind blows against the wall, but not during "suction".
Another possible option i was thinking was to grout the top 2 or 3 cores down throughout the wall length to cancel out the uplift. It will make the wall top heavy, but if it works, why not?
Also, there are some vertical and diagonal cracks on the wall. This is kind of the main reason why i want to reinforce the wall.
what do you guys think?