Reinforced Concrete Retaing Wall Design
civilman123
Hello everyone.
For the design of a cantilever retaining wall with:
1) vertical expansion joints every 30m (across the length of the structure) and
2) vertical partial contraction joints every 10m (across the length of the structure - 50% reinforcement continues through the joint)
3) The above joints will also apply to the foundation slab of the wall
To calculate the earth pressure area for the design will I consider only the length between the expansion joints?
Many thanks
Below my comments ,
1- vertical expansion joints could be every 30m ( depending on temperature , shrinkage of concrete ...)
2- vertical contraction joints normally provided at intervals not exceeding 7.5 m.
3- Not necessarily. The foundation is buried so , the EJ could be provided with longer sections.
The calculation is performed for unit width , ( 1.0 m)
Use it up, wear it out;
Make it do, or do without.
NEW ENGLAND MAXIM
1) vertical expansion joints every 30m (across the length of the structure) on NYSDOT projects we usually limit this to 90', 27 m
2) vertical partial contraction joints every 10m (across the length of the structure - 50% reinforcement continues through the joint)[COLOR=]30', 9m for contraction joints but we don't run the bars thru[/color]
3) The above joints will also apply to the foundation slab of the wallexpansion joints through footing but not contraction joints
To calculate the earth pressure area for the design will I consider only the length between the expansion joints?typically we design on a per foot basis
We typically use complete expansion joints through the wall only (not the footing) and space them around 100 ft (30m).
Our crack control joints (contraction joints) typically run at 10 ft. (3m) spacing. We have both maintained horizontal reinforcement though the joint and also sometimes cut 1/2 the bars.
