sentrifice
Mechanical
- Apr 5, 2023
- 25
Hi All,
I am working on foundation design for a Battery Storage enclosure and had some concerns. The design will go to a senior for review but for my own development I'm trying to take it to completion.
Background
The battery enclosure is a modified and braced shipping container, designed by others (8' x 30' x 9.5' tall). Total weight = 70 kips. Installation is in California so seismic loads are considered.
Current Design
Right now I have the foundation design as a 11' x 33' x 1.5' thick slab, with a bottom mat of #8 rebar 16" O.C. each way. The container will be set directly on the pad and anchored with 14 anchor brackets using epoxy anchors.
The bulk of my analysis was done by modeling the foundation as an isolated footing, where the pedestal is the width and length of the enclosure, and the footing is the size of the proposed foundation. I checked the following against code: soil bearing, overturning, sliding, flexure, one and two way shear, and minimum reinforcement.
Everything is checking out as far as code calculations go, and I've scoured the building codes for quite a while, but I feel like I'm missing something.
To double check myself I also modeled it as a "beam over elastic foundation" using the subgrade modulus in the geotech report and it showed max deflection of 0.124".
Question
Is there any reason to have a top mat of rebar? There is no calculated uplift or tension on the top of the slab. The anchor bolts also do not require any reinforcement since the anchor loads are low enough. One concern I have is of some kind of settlement related issues that might put the top into tension or cause cracking. The geotech report says that strip footings should be able to withstand 1/2" of differential settlement for a 30' footing. But I don't have a good feeling for if settlement is a concern for this type of installation.
Also, if anyone has any book recommendations on the topic I'd be happy to add to my growing collection.
I am working on foundation design for a Battery Storage enclosure and had some concerns. The design will go to a senior for review but for my own development I'm trying to take it to completion.
Background
The battery enclosure is a modified and braced shipping container, designed by others (8' x 30' x 9.5' tall). Total weight = 70 kips. Installation is in California so seismic loads are considered.
Current Design
Right now I have the foundation design as a 11' x 33' x 1.5' thick slab, with a bottom mat of #8 rebar 16" O.C. each way. The container will be set directly on the pad and anchored with 14 anchor brackets using epoxy anchors.
The bulk of my analysis was done by modeling the foundation as an isolated footing, where the pedestal is the width and length of the enclosure, and the footing is the size of the proposed foundation. I checked the following against code: soil bearing, overturning, sliding, flexure, one and two way shear, and minimum reinforcement.
Everything is checking out as far as code calculations go, and I've scoured the building codes for quite a while, but I feel like I'm missing something.
To double check myself I also modeled it as a "beam over elastic foundation" using the subgrade modulus in the geotech report and it showed max deflection of 0.124".
Question
Is there any reason to have a top mat of rebar? There is no calculated uplift or tension on the top of the slab. The anchor bolts also do not require any reinforcement since the anchor loads are low enough. One concern I have is of some kind of settlement related issues that might put the top into tension or cause cracking. The geotech report says that strip footings should be able to withstand 1/2" of differential settlement for a 30' footing. But I don't have a good feeling for if settlement is a concern for this type of installation.
Also, if anyone has any book recommendations on the topic I'd be happy to add to my growing collection.