I often have to design residential basement concrete walls that are taller than 10 feet.
The way I read the IRC and ACI 332, those codes only apply to walls less than 10 feet and ACI 318 has to be used if the wall is taller.
ACI 318 has minimum reinforcement requirements for both vertical and horizontal bars and maximum spacings.
So if a 10" wall is 9'-11 7/8" I can use plain concrete according to ACI 332 Table 8.2.1.3b with 30 pcf lateral but if the wall is 10'-0 1/8" I have to use at least #4's @ 16" o.c. vertical and #4's @ 10" o.c. horizontal based on ACI 318 14.3.2 and 14.3.3.
ACI 318 14.2.7 says minimum reinforcement in 14.3 can be waived if structural analysis shows adequate strength and stability. How do I do that? Is there a maximum spacing that can be used like the 6t in ACI 530? Do I have to worry about crack control? If I have bars spaced 48" would the reinforced concrete shear strength apply or would I need to use the plain concrete strength (a coefficient of 2 vs 4/3)? Do I just wave my hand at it and say it will work?
Any help or ideas will be appreciated. The contractors I work with don't like it when I call out vertical and horizontal bars.
Thanks
The way I read the IRC and ACI 332, those codes only apply to walls less than 10 feet and ACI 318 has to be used if the wall is taller.
ACI 318 has minimum reinforcement requirements for both vertical and horizontal bars and maximum spacings.
So if a 10" wall is 9'-11 7/8" I can use plain concrete according to ACI 332 Table 8.2.1.3b with 30 pcf lateral but if the wall is 10'-0 1/8" I have to use at least #4's @ 16" o.c. vertical and #4's @ 10" o.c. horizontal based on ACI 318 14.3.2 and 14.3.3.
ACI 318 14.2.7 says minimum reinforcement in 14.3 can be waived if structural analysis shows adequate strength and stability. How do I do that? Is there a maximum spacing that can be used like the 6t in ACI 530? Do I have to worry about crack control? If I have bars spaced 48" would the reinforced concrete shear strength apply or would I need to use the plain concrete strength (a coefficient of 2 vs 4/3)? Do I just wave my hand at it and say it will work?
Any help or ideas will be appreciated. The contractors I work with don't like it when I call out vertical and horizontal bars.
Thanks