Had an interesting situation pop up. Thought it might be worth mentioning here in case any of you ran across a similar situation.
The building is a large one. Has some rather shallow 60' plus span scissor trusses on it. The building has a hip roof, which further complicates things.
Either the architect or EOR figured some bearing would be needed on the shallowest trusses, so they put a bearing wall in near the hip end.
The last truss that hits the interior bearing has about 1/4" of deflection. The next truss that's clear span has 3" of deflection. (All deflection numbers are for total load)
The specs call for a total load deflection limit of L/240. On a 60' truss that's roughly 3".
So technically, the trusses work. They meet the deflection criteria in the specs. But no way in hell is that a good idea.
I was not involved in the job until yesterday. A guy asked me to look at the job and see what I thought. I suggested referring it back to the architect and EOR to see what they want to do. That's not a problem we can solve.
The building is a large one. Has some rather shallow 60' plus span scissor trusses on it. The building has a hip roof, which further complicates things.
Either the architect or EOR figured some bearing would be needed on the shallowest trusses, so they put a bearing wall in near the hip end.
The last truss that hits the interior bearing has about 1/4" of deflection. The next truss that's clear span has 3" of deflection. (All deflection numbers are for total load)
The specs call for a total load deflection limit of L/240. On a 60' truss that's roughly 3".
So technically, the trusses work. They meet the deflection criteria in the specs. But no way in hell is that a good idea.
I was not involved in the job until yesterday. A guy asked me to look at the job and see what I thought. I suggested referring it back to the architect and EOR to see what they want to do. That's not a problem we can solve.