Relay contact life

Status
Not open for further replies.

rawelk

Industrial
Apr 11, 2002
72
When reading through manufacturer's specifications for electromagnetic relays there is almost always a 'mechanical life' spec, often an electrical life spec for non-inductive loads, and sometimes one for inductive loads.

In this case, I'm looking at a Phoenix Contacts #2961105 relay used in their new "PLC" line of extremely small DIN rail mounted relay terminal blocks. It also has what appears to be a Tyco/Schrack part# (REL-MR- 24DC/21), uses AgSnO contacts rated for 6A/250VAC, and is given a mech life estimate of 20 million operations.

They also have an 'opto' (transistor) output DC module #2965595 rated for 3 amps.

In my application (driving a small pneumatic solenoid valve; don't know the specs, but it is 24 VDC, and looked to be on the order of 10 to 15 watts) it'll be cycled on about 4200 times per hour with a duty cycle on the order of 20 to 40%.

The machine was originally equipped with relay modules, but I'm planning on replacing them with the opto modules - relays just aren't going to hold up ;)

I'm wondering about several things ...

1). What does a manufacture consider 'life'? Is this similar to how bearing life is specified (i.e. - "B10" life, where 10% of the units are estimated to have failed by the specified time)?

2). Is there any rule-of-thumb for derating mechanical control relays subject to high cycle rates?

3). Solid state modules don't have a mechanical cycle life spec, and very few are given even an electrical one. For purposes of EM vs. SS estimated life comparisons I've typically used 300 million operations for a solid-state module. Does this sound like it is in the right ballpark?
 
Replies continue below

Recommended for you

4200 cycles per hour is more than once every second. The electrical life of a mechanical relay will be limited. The solenoid is inductive, the electrical life will be further limited.

Use solid state. Google on: odc modules -- for several vendors. Install a high speed diode across the solenoid for reduction in the surge during turn OFF. The cycle life of a solid state odc module is massive.
 
Thanks, Mike.
Yes, indeed, 4200 operations per hour is 70 cycles per minute.

I will be using their #2965595 opto-isolated module for replacement of the existing EM relays, and the engineer I spoke with indicated they've built a suppression diode into the module.
 