Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Relay Operation 1

Status
Not open for further replies.

jrrocks

Mechanical
Aug 13, 2018
58
There are two machine A & B which are running simultaneously. Both machine can provide 24V output when running. By using output of these machines I want to operate 3rd Machine C, provided following condition -
if both or Any of the machine A & B is running, machine C should operate
if both machine A & B shutoff, machine C also to be shut off.

Here, A & B are air supply terminal boxes and C is the condenser unit.
 
Replies continue below

Recommended for you

I think you answered the question yourself. But here's a simple diagram that doeas what you described:

Macine_A_or_B_starts_C_1_jnx9xg.png


This diagram assumes that your +24 V signals (from machine A and B) are delivering (not sinking) an output current - aka PNP or Active high outputs.

The diodes (Arrows in the diagram) can be 1N4007 or any variety

The asterisk shows a free-wheeling diode that may be nice to have to avoid inductive kick-backs.

Use a standard "Ice Cube" or 11-pole socket relay with a 24 V DC coil.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
Let me correct your wordings..
Not couple of years...... but 29hr: 35min: 41sec : 05ms
 