- Sep 13, 2013
- 7
I have an application where among other things I need to control some solenoids and motors from a PLC. One of the project requirements is that I must keep leakage current as low as possible and therefore I must use relay outputs instead of solid state.
The datasheet for the module says that each output has a 2A switching capacity for inductive loads. Some of my loads are 10W 24VDC solenoids, 30W 230VAC fans, and 3W 230VAC motors. Is it ok to power these loads directly from the PLC outputs assuming that I provide the appropriate surge suppression?
I can see the argument for an intermediate relay because it’s easier to replace one relay than a whole module if something fails. However as always space is a concern and it would be convenient to use the relay outputs directly if possible.
Please share any comments or practical experience that you have. Thanks!