chuckd83
Electrical
- Oct 2, 2014
- 42
In the medium voltage world, we set our pickup above equipment ratings to allow the customer the flexibility of temporary overloads. We protect against short-circuit and not overload.
For cable, this is allowed per NEC 240.101(A).
For transformers, NEC Table 450.3(A).
Is this discussed anywhere with respect to the breaker itself (setting the pickup above its continuous rating)? I've looked through the Red Book, Buff Book, ABB T&D book.
For cable, this is allowed per NEC 240.101(A).
For transformers, NEC Table 450.3(A).
Is this discussed anywhere with respect to the breaker itself (setting the pickup above its continuous rating)? I've looked through the Red Book, Buff Book, ABB T&D book.