Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Relay Schlumberger RSAS 3750

Status
Not open for further replies.

Eng.Edward.M

Electrical
Mar 5, 2021
13
0
0
BR
Good morning everyone!
I have a doubt about how the adjustment is made in the RSAS 3750 relay.
Example: TC - 500/5
Ip - timed starting current
scale 1 - 2
steps 0.2
With this I can adjust the KpA / KpB / Kpc to 1/1.2/1.4/1.6/1.8/2
We have the equation Ip = Kp x In
Therefore, if I select 1.2, the result will be Ip = 1.2 x 5 x 100(RTC) = 600A

Ii - instantaneous inrush current
scale 1 - 5
steps 1
C = 4
With this I can adjust the Ki to 1/2/3/4/5
We have the equation Ii=Ki x C x Ip
So, if I select 2, the result will be Ii= 2 x 4 x Ip(1.2 x 5) x 100(RTC) = 4800A
 
Status
Not open for further replies.
Back
Top