Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Reliability of gel-cell (VRLA) batteries 2

Status
Not open for further replies.

wde3477

Electrical
Jun 26, 2001
12
Our insurance inspector voiced concerns over our recent installation of VRLA batteries, and suggested a capacity test even though the batteries are less than one year old. This is our first VRLA set on the larger systems (2000 Amp-hour) - capacity tests are currently scheduled for our Lead-Acid sets every five years. The research I did prior to specifying VRLA did not reveal any serious problems with this style battery - assuming proper maintenance and operation is done - and the pricing and delivery made them especially attractive. I would like to hear of any negative experiences or known problems with this type of battery that would support our inspector's concerns.
 
Replies continue below

Recommended for you

I have mixed views on VRLA. We use VRLA batteries extensively in our company. In 1989 we began using 20 year batteries. To date, they have been less than satisfactory - some failing between 7 and 11 years. The kicker was that when they failed they had a tendancy to fail in an "open circuit" state ... that is to say, zero current flow. Not the ideal failure mode for a UPS system. I believe this is the history your insurance underwriter is concerned about.

I would speculate that many of the VRLA batteries were not maintained as well as flooded batteries they were intended to replace. Many of the first generation batteries were marketed as "Maintenance Free" in which many users took it literally ... just like your car battery. Clearly they were not Maintenance free but more like "reduced maintenance". Since the mid 90's, many manufacturers and vendors have avoided the "free" aspect and improved their literature around proper maintenance.

As I understand it, the battery technology of today is considered "third" generation, in which manufacturing process have been perfected and cell design improved which virtually eliminates the old failure modes. Most of our original "First" generation VRLAs have been replaced. Batteries installed since the late 1990's have performed more predictably with no open failures.

To mitigate this risk to our business, we have switched to:
- 10 year batteries,
- parallel strings
- annual testing (pending the number of cycles the batteries are put through per year)

This established the right balanced of maintenance cost with capital cost and allows us to leverage newer and improved VRLA technology (or it's future replacement) as it is perfected. If you take the right approach to managing risk, you should be able to address the concerns with your underwriter.

 
Kasane,

Only just read your post - couldn't have put it better myself. Exactly my sentiments after 20 years in the business. Nice one!
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor