AlbertaMecchie
Mechanical
- Feb 17, 2021
- 19
Working on a project, and the request is to move a Fisher H203 downstream of a 4" NPS 300# isolation valve on a natural gas pressure reducing station. I'm not sure yet what the logic behind the request is. Inlet pressure to the series-installed main and monitor regulators (both 600# rated) is 1035 psi. The Fisher H203 is located on a 1" branch just downstream of the main and monitor pressure regulators. Maximum set pressure on a 1" Fisher H203 is 300 psi, H203 valve body is rated for 400 psi. New set pressure on relief valve will be around 72-75 psi. If the working and monitor regulators fail, pressure upstream of the relief valve could start heading up towards maximum line pressure of 1034 psi. My concern is if the regulators fail, with the Fisher H203 moved to this new position downstream of the 4" isolator, if an operator closes that 4" NPS 300# isolator, the pipe flange and inlet valve flange at the isolator could be over-pressured, 300# flanges are good only to 749 psi operating. Any thoughts on this ? I think the H203 should be left where it is with new set pressure of 72-75 psi - or is the 400 psi body rating of the H203 (400 psi) a concern even though it's max spring (relief) setting is 300 psi ? It's tough to find these pop-type small relief valves with body ratings up to 1034 psi and the lower required set pressure of 72 psi. Just looking for 2nd views on this. Thanks.