Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Relief Valve Sizing

Status
Not open for further replies.

Cool_Controls

Electrical
Feb 5, 2020
150
I have come across a shell and tube heat exchanger in the basement of my office building that has no pressure relief valve on it and I would like to know how to select the right size relief valve for it. The heat exchanger provides hot water for the buildings HVAC system, 15psi steam on the shell side, 30psig water in the tubes, centrifugal pumps. Its always been my understanding that the relief valve in this context protects against thermal expansion either from a blocked in condition or failed expansion tank. A tube failure on these units just results in heating water being lost into the condensate line and making the boiler plant operators annoyed at the hard water coming back to the plant.
 
Replies continue below

Recommended for you

The shellside PSV should be adequately sized to handle (blocked in) tube rupture if the max normal water pressure is higher than design pressure of the shellside - a failed or blocked steam condensate trap is a credible operating scenario.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor