From my reading of API 520 for fire contingency, it seems that regardless of relief valve set pressure, the value for P1 (relieving pressure) used in the calculations is MAWP + allowable overpressure + 14.7 psia. I'm using Table 5 as the example here. MAWP is 100 psig, set is 90 psig, allowable (21% above MAWP) is 31 psi making the relieving pressure 135.7 psia. In a previous discussion, thread798-166100, pleckner explains, "...The PSV will pop open if the internal vessel pressure reaches this set pressure. However, the full relieving flow from the vessel will only occurr when the internal pressure reaches 21% of this set pressure. ASME allows a vessel in a fire to over pressure 21% above design or MAWP (Maximum Allowable Working Pressure)."
As I've cruised over other examples through various vendor literature, that subtelty of the overpressure being based on MAWP can get lost and overpressure can be based on set pressure. Okay, if that is done, full relieving capacity is obtained somewhere before 121% of MAWP is reached, right? Further, my relieving temperature should be based on vapor pressure equal to relieving pressure, right? Well, if I'm using overpressure based on 121% of MAWP and my set pressure is significantly lower than MAWP, say half, for example, physically my relieving temperature is really somewhere below that temperature used in the calculation. How does this effect the reality of what is happening as the valve is relieving?
It seems that using a lower value for P1, and the associated relieving temperature, just gets you to full relieving capacity faster and oversizes your valve. Any additional though to help me get my mind around this?
Thanks for the help. What a great forum.
MechBRR
As I've cruised over other examples through various vendor literature, that subtelty of the overpressure being based on MAWP can get lost and overpressure can be based on set pressure. Okay, if that is done, full relieving capacity is obtained somewhere before 121% of MAWP is reached, right? Further, my relieving temperature should be based on vapor pressure equal to relieving pressure, right? Well, if I'm using overpressure based on 121% of MAWP and my set pressure is significantly lower than MAWP, say half, for example, physically my relieving temperature is really somewhere below that temperature used in the calculation. How does this effect the reality of what is happening as the valve is relieving?
It seems that using a lower value for P1, and the associated relieving temperature, just gets you to full relieving capacity faster and oversizes your valve. Any additional though to help me get my mind around this?
Thanks for the help. What a great forum.