mfstructural
Structural
- Feb 1, 2009
- 230
I'm currently working on a project where we are pouring footings below some existing columns in the basement of a 4 story building in Chicago. The issue came about because the building owner hired a contractor to repair the wood columns which were rotted at their bases from years of moisture absorption. The contractor proceeded to cut off the bottom 6 inches or so and wedge a paver brick between the basement slab and bottom of column. The slab was excavated around a couple of the columns and there are no footings per the owner. I have not been to the site. So we will be pouring footings under each column. the question I have is regarding the wood columns though. This is a four story building, with the first story serving as commercial space (furniture store) and rest of the levels as residential. I'd prefer steel in case the basement floods or there is water, the steel will not decay as quickly as a wood column wood (at least that's what I think). But I don't want to do it if it's not necessary. To evaluate the existing columns I'd assume the lowest allowable for a wood column in compression. The column is a 6x6. The city is specifially requesting an engineer to evaluate the columns and their supports, more the supports. I'm not sure I'd be ok leaving them (and building a pedestal on the footing) even if they are ok. I am more comfortable with steel for this application, but it's an expense for the building owner and if I can avoid it and the columns are ok I'd leave them if there was a healthy margin.