SparkOmatix
I have an Allen Bradley Size 3 Starter with a maximum HP rating of 50 HP, an overload block adjustable to 75 Amps, a 3P 100 Amp Breaker, and (3) #4 THHN Wires. The Compressor motor is approximately 200 linear feet from the MCC panel. This is the current configuation on a 40HP motor. I am looking to replace the 40HP motor with a 50HP motor. My question is this...
Do I look at the cable capacity from a 75C (85A) standpoint or a 90C (95A) standpoint.
Some values I calculated are as follows:
HP = 50
kVA = 53.98
Voltage = 480
FLA = 65
Demand Factor = .8
Diversified Amps = 52
Diversified KVA = 43.18
Breaker Starter Size = 100
Over Load Current = 75.75
Max Motor AMPS = 93.44
If I go with the 75C approach, I would have to upsize the cable to a #3, yes? However, the 90C view says I'm ok with a #4, no?
Does the voltage drop need to be no greater than 3% or is 5% acceptable?
Any insite is appreciated.
HP = 50
kVA = 53.98
Voltage = 480
FLA = 65
Demand Factor = .8