mfstructural
Structural
- Feb 1, 2009
- 230
I am currently looking at a building where our client needs to replace a portion of the lintels. It's a 3 wythe masonry building The original lintel was constructed of a steel WF beam with a plate welded to the bottom. The interior portion of the lintel is intact, with no corrosion. The outer portion of the lintel, including a portion of the bottom flange of the steel plate supporting the outermost wythe of brick is heavily corroded. The plan is to cut off the corroded portion of the plate and also a small portion of the flange that is corroded and place a steel angle across the opening. There are 2 different sizes of openings on the building, 5' and 9'-6". A L5x3 or L6x4 would work for the 5' opening. The issue is with the 9.5' opening. I'm thinking of placing a L6x4x3/8 angle across this 9.5' opening and welding it back to the web of the original lintel with 6" long L4x4 angles at 24" on center. This will prevent the angle from rotating and then I will be able to use the full strength of the angle. There is approximately 5' of brick above each 9.5' opening, except at the parapet where there is about 8' of brick over the opening. Any other recommendations? How have others approached repairing damaged/corroded lintels in the past?
thanks
thanks