apollowolfe
Mechanical
- Jul 6, 2019
- 7
Hello, I have not been in the industry very long and wanted some feedback on a design that took place at work.
We had about a 9,000 SF single floor office building in Tennessee with no major loads. The original equipment was a 24,000 CFM AHU and a 60-ton air-cooled chiller. The client wanted to switch to a DX system while leaving all the current ductwork and VAVs. The load I ran for the building yielded about 23 tons of cooling. The lead engineer of the project ended up just getting a new 24,000 CFM AHU and a 60-ton VRF system. Would you consider this approach acceptable, and if not, what would be a better solution?
Thank you for the Input,
We had about a 9,000 SF single floor office building in Tennessee with no major loads. The original equipment was a 24,000 CFM AHU and a 60-ton air-cooled chiller. The client wanted to switch to a DX system while leaving all the current ductwork and VAVs. The load I ran for the building yielded about 23 tons of cooling. The lead engineer of the project ended up just getting a new 24,000 CFM AHU and a 60-ton VRF system. Would you consider this approach acceptable, and if not, what would be a better solution?