I always depend on the following equation in calculating the required KW for the motor of the pump (Pumped Fluid : clod water):
KW (Absorbed power) = (H x Flow)/ Pump Eff. x 367
Motor power = P abs. X Motor Eff.
Then I check with the suppliers the availabe motor size that close to my calculation and I CHOSE one with higher rated power. Inaddition I ask for 1.15 SF ,
Do I need to be more strict in the calculation ? is there are any other points I forget to consider in may calculation to the KW?