I completed the HVAC design for a church in my area a while back. Currently there is a disagreement over the neccessity for outdoor (ventilation) air. I'm in FL and the current Florida code is based upon the 2003 IMC.
Section 403.3 of the 2004 Florida Mechanical Code states, “Ventilation systems for other than Group R-3 (one- and two-family dwellings), shall be designed to have the capacity to supply the minimum outdoor airflow rate determined in accordance with Table 403.3 based on the occupancy of the space and the occupant load or other parameter as stated therein. The occupant load utilized for design of the ventilation system shall not be less than the number determined from the estimated maximum occupant load rate indicated in Table 403.3. Ventilation rates for occupancies not represented in Table 403.3 shall be determined by an approved engineering analysis. . .”
The mechanical contractor on this project has convinced the owner that because Table 403.3 does not explicity list churches, they are exempt from vetilation air requirements. I pointed out to the owner that the table does not list everything and that the paragraph states "Ventilation rates for occupancies not represented in Table 403.3 shall be determined by an approved engineering analysis" which I did. The owner countered that some county official has sided with the contractor in this case.
I believe that counties and municipalities can have their own requirements independent of the state, but this doesn't seem right at all. I have asked the owner to secure a letter from the county office which states that ventilation air is not required. If they are able to get this letter, I will then ask the owner for a letter stating that they have asked me to not include ventilation air in the design and recognize the health risks associated with this decision. At that point, I suppose I will remove the outside air and resize the equipment. Can anybody offer any advice on this situation?
Let me add that I have emailed the state Building Codes and Standards Office looking for their input as well.
Section 403.3 of the 2004 Florida Mechanical Code states, “Ventilation systems for other than Group R-3 (one- and two-family dwellings), shall be designed to have the capacity to supply the minimum outdoor airflow rate determined in accordance with Table 403.3 based on the occupancy of the space and the occupant load or other parameter as stated therein. The occupant load utilized for design of the ventilation system shall not be less than the number determined from the estimated maximum occupant load rate indicated in Table 403.3. Ventilation rates for occupancies not represented in Table 403.3 shall be determined by an approved engineering analysis. . .”
The mechanical contractor on this project has convinced the owner that because Table 403.3 does not explicity list churches, they are exempt from vetilation air requirements. I pointed out to the owner that the table does not list everything and that the paragraph states "Ventilation rates for occupancies not represented in Table 403.3 shall be determined by an approved engineering analysis" which I did. The owner countered that some county official has sided with the contractor in this case.
I believe that counties and municipalities can have their own requirements independent of the state, but this doesn't seem right at all. I have asked the owner to secure a letter from the county office which states that ventilation air is not required. If they are able to get this letter, I will then ask the owner for a letter stating that they have asked me to not include ventilation air in the design and recognize the health risks associated with this decision. At that point, I suppose I will remove the outside air and resize the equipment. Can anybody offer any advice on this situation?
Let me add that I have emailed the state Building Codes and Standards Office looking for their input as well.