Norm01
Mechanical
- Apr 18, 2008
- 27
I have large building with a number of sprinkler headers located at various locations. The building fire protection system is to be supplied with a reservoir and a vertical turbine pump. Based on hydraulic calculations of the sprinkler systems, the system futhest from the water supply has a system demand of 520 gpm @ 125 psi. A system closer to the water supply has a system demand of 688 gpm @ 105 psi. Both systems are ordinary hazard occupancy with a water supply duration of 60 minutes. In order to size the reservoir and pump system is it a matter of sizing the reservoir to meet the demand of the 688 gpm system (i.e. 41,280 gal.) and then size the pump to meet the pressure requirements of the 520 gpm system ?