simonswb6
Civil/Environmental
- Oct 16, 2006
- 7
Came upon this and was looking for some different opinions. This is a 10ft high, by 8ft wide window array. To me, it appears that the dead load from the top 2 rows of windows is being dumped onto the bottom row of windows. The only thing holding the window sill plate into the wood column for the upper 2 rows of windows is nails, no hangers, no jack studs, nothing. I recommended re-framing with steel posts and weld some steel angles so the sill plates would have a seat to fit into. If that is too expensive, make up some steel angles and lag bolt into the existing wood posts, and create seats, same effect as above. In my opinion, if the basement settles or you get some high wind loads, there could be some problems here.