ThorenO2
Structural
- May 24, 2019
- 51
Hello,
I'm designing a house where the architect wants "open concept" living for the owners. This has resulted in a 4-ply 16" LVL spanning 24' picking up 30psf LL from 2 upstairs bedrooms and part of a hallway. The LL on the beam amounts to an incredible 11,000 lbs, where I've justified a LL reduction - no way can they fit that much stuff in the space. HUD's Residential Design Guide; however, uses a formula limiting the reduction to 25%, which still leaves tons of weight to design for. My question is, what are the opinions on designing to a 1" total deflection (L/288 < L/240) and 0.6" LL deflection (L/476 < L/360), with my opinion wavering between "no sweat - the calc meets code" or "that's going to leave a low spot in the floor at the adjacent joists". I appreciate any insight - thank you.
I'm designing a house where the architect wants "open concept" living for the owners. This has resulted in a 4-ply 16" LVL spanning 24' picking up 30psf LL from 2 upstairs bedrooms and part of a hallway. The LL on the beam amounts to an incredible 11,000 lbs, where I've justified a LL reduction - no way can they fit that much stuff in the space. HUD's Residential Design Guide; however, uses a formula limiting the reduction to 25%, which still leaves tons of weight to design for. My question is, what are the opinions on designing to a 1" total deflection (L/288 < L/240) and 0.6" LL deflection (L/476 < L/360), with my opinion wavering between "no sweat - the calc meets code" or "that's going to leave a low spot in the floor at the adjacent joists". I appreciate any insight - thank you.