skdesigner is correct. You can not use residential sprinklers outside the dwelling units with the exception of corridors.
From NFPA #13 (2002):
8.4.5 Residential Sprinklers.
8.4.5.1* Residential sprinklers shall be permitted in dwelling units and their adjoining corridors provided they are installed in conformance with their listing.
A.8.4.5.1 The response and water distribution pattern of listed residential sprinklers have been shown by extensive fire testing to provide better control than spray sprinklers in residential occupancies. These sprinklers are intended to prevent flashover in the room of fire origin, thus improving the chance for occupants to escape or be evacuated.
The protection area for residential sprinklers is defined in the listing of the sprinkler as a maximum square or rectangular area. Listing information is presented in even 2-ft (0.65-m) increments from 12 ft to 20 ft (3.9 m to 6.5 m). When a sprinkler is selected for an application, its area of coverage must be equal to or greater than both the length and width of the hazard area. For example, if the hazard to be protected is a room 13 ft 6 in. (4.4 m) wide and 17 ft 6 in. (5.6 m) long, a sprinkler that is listed to protect a rectangular area of 14 ft × 18 ft (4.5 m × 5.8 m) or a square area of 18 ft × 18 ft (5.8 m × 5.8 m) must be selected. The flow used in the calculations is then selected as the flow required by the listing for the selected coverage.
One thing I enjoy about this forum is if I am wrong, often enough I am, my error is quickly pointed out so here goes.
In an
NFPA 13 system you can use residential sprinklers inside the dwelling unit but be careful that the density meets the .10 gpm requirement per NFPA #13.
Consider the VK466 - Residential Pendent Sprinkler (K5.2) residential sprinkler.
In an 18'x18' room the discharge requirement is 17 gpm @ 10.7 psi for NFPA #13R systems but 17 gpm hardly satisfies the requirement of NFPA #13 which require a discharge of 32.4 gpm @ 33.5 psi in order to achieve the .10 gpm density.
If the room is long and narrow, say 18'x8', the discharge would have to be 14.4 gpm to achieve the .10 density but the data sheet requires 17 gpm @ 10.7 psi in accordance with the listing for residential use.
Basically you use the higher of the two which, in the case of the 18'x8' room, would be 17 gpm @ 10.7 psi.
For Georgia I can say the state fire marshal will require the higher of the two discharges and the higher of the two is what I have always used inside or outside the dwelling units.
As for the corridor I believe the standard requires only four sprinklers need be calculated but here in Georgia the state fire marshal requires five heads calculated and it doesn't matter if the system is designed per NFPA #13 or #13R.
Is Georgia correct in requiring a density of .10 gpm in or out of the dwelling units themselves?