TRAK.Structural - I went from doing almost solely DOT MSE/SRW walls to a lot more residential over the last couple years. Here are a few things I have learned about smaller residential walls:
- Regardless of what you specify for the reinforced fill zone, there is a good chance the contractor will just install 12" of crushed stone followed by onsite fill, even if it doesn't meet your specified reinforced fill. When checking designs, I always do a "what if" check to see if I am still comfortable with the design if onsite fill gets replaced with my specified reinforced fill.
- I specify that 3rd party should test the foundation and fill soil, and inspect the leveling pad, fill placement, and geogrid placement. And geogrid should extend past the face to confirm the spacing (can be cut after construction). I would say only about half of small residential projects does this go as specified.
- There is a chance you will never hear anything after you send off drawings, then a while later get a call from the contractor asking for a sealed form that the wall was built to plan (after they had no inspections or testing, maybe a couple field photos). Be prepared for how you will respond to this.
- For shorter walls, I start with the USDA web soil survey to get a general idea of soil layers, groundwater depth, etc. then have the contractor verify this prior to design, then specify testing/inspection during construction.
Here are a few general pointer on design:
- SRW grid lengths are typically controlled by sliding or pullout. You can lengthen the gris to ~0.8*H before there is minimal reduction in applied bearing pressure because you are approaching the weight of the soil itself. I always show the applied bearing pressure at each change in grid length that the foundation must meet.
- I tried to use the NCMA software and hated it. I also tried Allan Block's software and found it glitches too often for me to feel comfortable with the results, and only applies to one manufacturer. I like to use Vespa2 by CTi Software because you can design the whole wall in one go, then export the full wall elevation view and cross sections into CAD. It has all the common blocks and grid testing preloaded, and you can export to ReSSA or Gslope for global analysis. I have also worked closely with their team on a client specific program and they know their stuff. Anything non-standard I check in MSEW+. Vespa2 has some training videos, and I have one I created for my team that I can share.
For general notes, Allan Block and Keystone both have a lot of great resources. Also look at some of the DOT's APL drawings (FDOT APL section 548, for instance).