Residual pressure 1

Status
Not open for further replies.

beameupscotty

Civil/Environmental
Aug 7, 2003
17
I am confused whether 8 psi or 15 psi should be used for private residential dwellings (4-plex). Code book I have says 15 psi for flushometer valves and 8 psi for flush tanks. Plans don't call for flushometer valve toilet, so do I automatically use 8 psi or am I missing something?

Thanks in advance for your time.
 
Replies continue below

Recommended for you

The code book is referencing the minimum pressure required to operate the fixture.

You use this to get a uniform pressure loss so you can size your water piping.

You should use the 8 psi since you are not going to use flush valves. If the plans change and you use flush valves, use 25 psi for the flush valves. 15 is too low.
 