What would you classify the R value for a 4 story building, laterally supported utilizing X-braces? I am using the IBC 2000 code.

TIA,
Mark
 
Replies continue below

Recommended for you

The walls are light gauge steel studs.

 
It depends on your framing materials and your desired degree of detailing.

If you have a steel framed building, in Table 1617.6, you would fall under "Building Frame Systems" (item 2).

Now, with X braces, you could either be type C, Special concentrically braced frames (R = 6); or type D, Ordinary Concentrically braced frames (R = 5)

The special frames require a higher degree of detailing vs. the ordinary.
 
I get the impression from the second post that this is not a structural steel braced frame system. Do you have metal stud walls with diagonal strap tension bracing? If so, the R factor would be lower. The closest thing in the IBC would be Type 1L in Table 1617.6, "Light frame walls with shear panels-all other materials" (R=2). In the UBC, the system is Type 1.3 in Table 16-N, "Light steel-framed bearing walls with tension-only bracing" (R=2.8).
 
Thank you both for the response.

Yes, Taro, the bracing is tension bracing on light gauge studs.

I also thought that R = 2 was the appropriate value. I just couldn't believe the seismic base shear would increase by 3!! After seeing some X-braces in the field, however, it does not seem like a bad idea at all. (Many braces were loose, poorly connected, etc...)
 
Taro / mjohan

Can you have tension ONLY braces for seismic in this condition? I thought that a minimum percentage of braces have to be split between tension/compression.
 
JAE,
Yes, the bracing is light gage flat strap bracing that carries tension only. That is why the R factor is so low. Better performance would be achieved by using structural panel sheathing (R=6).
 