Restricted Earthfault tripping

Status
Not open for further replies.

wilton2015

Electrical
Jan 7, 2016
2
please can someone explain why the REF relay on meant to protect a 60MVA 132/33KV transformer will trip whenever a 33kv line feeding from the transformer trips on Earth fault.
 
Replies continue below

Recommended for you

Less likely, but it could be due to a blue box if you don't keep up with manufacturer notifications on firmware updates.
 
Thank you all i am going back to site to look at the polarity, will update u
 
CT connection/polarity problem
Usually neutral CT, as ScottyUK said.

of course possible setting mistake.
 