XR250
Structural
- Jan 30, 2013
- 5,760
The contractor has the hook pointing toward the heel but add similar bottom bars to compensate. Is there a reason this is not OK?

Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Which case do you consider is mine, Celt83?
XR250 said:Is there a reason this is not OK?
KootK said:It's fundamentally bass-awards concrete detailing...
U76 has a toe length of just 4in (Tomfh said:In smaller walls with small toes there’s often little room to run a hook into the toe.
steveh49 said:no reinforcement on the tension face of the toe?
I don't believe so, in my understanding of a strut-tie approach turning the hook the other direction creates a compression strut from the curved bar node into the heel leading to a required vertical concrete tension tie around where the mid-depth crack is shown on the U73 specimen.Tomfh said:It's not hard to imagine that bar adding the missing ~30%
MotorCity said:If ACI's not worried about it, neither am I.
kootk said:...the 40% reduction associated with U74 reflects the fundamental nature of the situation having changed: it's now an anchorage problem rather than a reinforced concrete problem.