vato
Structural
- Aug 10, 2007
- 133
I got a soils report, after the foundation was designed for 2000 psf soil bearing and footing forms in place, and we have "slightly" expansive soils.
Now I am redesigning for 800psf min dead load and 3000psf maximum soil bearing. So far I have been able to use 6 square foot pads
spaced 8'-0" o.c. with a 4' deep grade beam. Most of the forms on the ground can be reused. Frost depth is 48" here with 100psf snow load, 10,000 ft elev.
The building is a one story wood framed structure. Not much dead load to work with.
Here is where I am scratching my head....
The east side of the building foundation was originally designed as a 5' tall retaining wall with 4' wide footer.
I can remove portions of the footer, similar to the rest of the foundation, and reinforce the wall as a grade beam between pads.
This will ensure the 800psf dead load but I am concerned about still retaining the soil with the voids required between footings using this approach.
Feels like I'm removing the concrete at the point of highest lateral pressure if I do this.
I am leaning toward voiding portions of the retaining wall footing, leaving an edge/soil contact on each side of the footer with a contact strip under the wall as well. My retaining wall would still work as a cantilever and allow some expansion beneath it, kind of like a waffle slab. Seems like someone has done this by now. It's not imperative that I reuse the forms on the ground, but I should be able to work it out.
Thanks in advance for your thoughts on this.
ps the foundation will have a perimeter drain as well as a drainage plane below the floating slab, and we will be spending more time and money on the geotech, before the forms are set next time.
Now I am redesigning for 800psf min dead load and 3000psf maximum soil bearing. So far I have been able to use 6 square foot pads
spaced 8'-0" o.c. with a 4' deep grade beam. Most of the forms on the ground can be reused. Frost depth is 48" here with 100psf snow load, 10,000 ft elev.
The building is a one story wood framed structure. Not much dead load to work with.
Here is where I am scratching my head....
The east side of the building foundation was originally designed as a 5' tall retaining wall with 4' wide footer.
I can remove portions of the footer, similar to the rest of the foundation, and reinforce the wall as a grade beam between pads.
This will ensure the 800psf dead load but I am concerned about still retaining the soil with the voids required between footings using this approach.
Feels like I'm removing the concrete at the point of highest lateral pressure if I do this.
I am leaning toward voiding portions of the retaining wall footing, leaving an edge/soil contact on each side of the footer with a contact strip under the wall as well. My retaining wall would still work as a cantilever and allow some expansion beneath it, kind of like a waffle slab. Seems like someone has done this by now. It's not imperative that I reuse the forms on the ground, but I should be able to work it out.
Thanks in advance for your thoughts on this.
ps the foundation will have a perimeter drain as well as a drainage plane below the floating slab, and we will be spending more time and money on the geotech, before the forms are set next time.