- Oct 22, 2019
- 77
I am reading one article about desigining a concrete retaining wall.
The As required for Stem is As: 2.26 in² per 1 foot.
Author use #9 each 4.5" (Center to Center)
Why AS is equal to 2.67?
As required is 2.26 in², so he should be using 3 #9 (3 in²)each 1 foot.
Any explanation?
Thanks and Regards