Hey guys, I'm currently working on designing a concrete base for a steel retaining wall. The wall will retain salt (density = 12kN/m^3, angle of friction of 30 degrees). The wall will be 6.5m high but the fill will be heaped to a maximum height of 18m. I tried designing it as if it weren't heaped but the thing keeps failing due to sliding. Is there a way to calculate Active pressure force due to a limited extent heaped material? Any resources that would help me would be greatly appreciated.
Certainly there is, use the Culmann method. Follow any text that explains active push through graphic statics.
If I am understanding your situation correctly, I use a chart out of the Naval Facility Manual, Figure 3: Active and Passive Coefficients for Sloping Backfill. You can find this online but I have forgotten the location.
Sounds like a condition where the backfill slopes up behind/above the retaining wall and then levels off. I use the trial wedge method to figure the active load for this type of retainage condition. Trial wedge is wonderfully simple.
I think boot is correct in there are also some charts in the NAVFAC design manuals, but I am not positive. They are free, just google Naval Facilities Design Manuals. I think it is Manual 7.2 or 7.3
Thanks for the help. This is exactly what I was looking for. The only concern I have is that the backfill is not sloping indefinitely, it has limited extent (peaks at a horizontal distance of 20m away from the wall at an angle of 30°) and according to an *old* copy of Reynold's reinforced concrete designers handbook, I need to treat this case slightly different. I've used 4 different methods(including the one mentioned here) on how to deal with the active force from a sloping backfill and every one of them fails due to sliding except for the case where I treat the section on slope above the wall between the failure plane (<α) as a triangular surcharge load. Thanks anyways guys.
Sounds like you may have to mobilize some passive soil pressure with a key. Sliding failures are nasty.
Maybe I have misunderstood what you are saying, but if accepted analysis methods indicate that the wall is not stable then you need to modify the wall design.
Modelling a stockpile as a vertical surcharge does not include all the effects. There is also a spreading force at the base of the stockpile, which will be transferred to the wall.
Doug Jenkins