Return air VFD fan control with return air static pressure

Status
Not open for further replies.

dubbed

Mechanical
Jul 17, 2006
37
Have a question on how to apply this correctly.
The return fan speed with be controlled with a static pressure transducer in the return duct.

my question is where to put the pressure xducer and is it suction that i need to measure.

This is what I'm using for supply duct pressure after the supply fan
Not sure if this will work for return.
 
Replies continue below

Recommended for you

ok nevermind. I read the control sequence wrong.
not sure what its goal is.
 
The goal is typically a high limit on suction side (say above 2") to disable the fans before you get a sucked in duct.
 