rockman7892
Electrical
- Apr 7, 2008
- 1,161
We are in the process of upgrading existing protection and controls in an industrial customers substation which brings in 230kV transmission voltage and steps it down to 13.8k and 4.16kV through the substation transformers. The existing 230kV SF6 breaker relays had 67 functions for monitoring fault current contribution from the plant to the utility primarily because the plant had local emergency generation at the 4.16kV level that could operate in parallel with the utility.
With the new upgrades the 4.16kv generators will not be able to parallel with the utility. Without this generation is there a need for a 67 function on the 230kV breakers? The plant does have several large synchronous motors (5000 hp) at the 4.16kV level which will contribute fault current to a fault on the 230kV system. Do these synchronous motors justify having a 67 function on the 230kV main breakers for faults on the 230kV system.
Do the 230kV breakers in this substation application typically have 27 and 81 tripping functions?
With the new upgrades the 4.16kv generators will not be able to parallel with the utility. Without this generation is there a need for a 67 function on the 230kV breakers? The plant does have several large synchronous motors (5000 hp) at the 4.16kV level which will contribute fault current to a fault on the 230kV system. Do these synchronous motors justify having a 67 function on the 230kV main breakers for faults on the 230kV system.
Do the 230kV breakers in this substation application typically have 27 and 81 tripping functions?