Reverse power relay

Status
Not open for further replies.

lavurk

Electrical
Dec 7, 2010
4
can anybody explain about reverse power relay?
 
Replies continue below

Recommended for you

Google probably can. Have you tried?


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
A reverse power relay is a wattmetric type of device that closes a contact and trips the generator breaker when the kW (MW) from a generator to the busbar goes negative, in otherwords goes into "motoring".

Motoring is not allowed for any generator as the prime mover will be affected: In a steam turbine there will be insufficienr steam flow to maintain temperature balance, if a diesel it will act as an air compressor, a hydro may begin to cavitate...

Usually a time lag of not more than 10 seconds is applied.

Motoring is caused by the prime mover itself, or the governing system having shut off the fuel (water) for some reason, or an operator error, usually when taking the unit off line, or even just after synchronizing to the busbar.

rasevskii
 
for steam turbines, Reverse Power relay logic has been added (recomended) to provide verification that the steam flow has been stopped BEFORE allowing the generator breaker to be open on a turbine trip.
 
Status
Not open for further replies.

Part and Inventory Search