JBF
Electrical
- Jan 17, 2003
- 1
I need to replace an old WH (now ABB) Reverse power relay type CW model 289B988A17 with a more sensitive one.
This one is on a steam turbine and has a pick up VA of 20W which is the relays minimum setting.
VT 4200:120 CT 2000:5
20 W is equivelant to about 485 kW motoring.
This is a single relay for a balanced system.
Per IEEE/ANSI 242 "Generator Protection" I would like to have a replacement relay with a pick up of about 2.5 W equivelant to about 60 kW motoring power.(20% motor power)
This would appear to protect 300 kW, 3% of rated prime mover.
There is no budget for a comprehensive digital generator relay.
Q1 Where can I find a sufficiently sensitive relay replacement?
Q2 Is there a direct replacement that will fit inot the FT-11 case?
Any thoughts?
This one is on a steam turbine and has a pick up VA of 20W which is the relays minimum setting.
VT 4200:120 CT 2000:5
20 W is equivelant to about 485 kW motoring.
This is a single relay for a balanced system.
Per IEEE/ANSI 242 "Generator Protection" I would like to have a replacement relay with a pick up of about 2.5 W equivelant to about 60 kW motoring power.(20% motor power)
This would appear to protect 300 kW, 3% of rated prime mover.
There is no budget for a comprehensive digital generator relay.
Q1 Where can I find a sufficiently sensitive relay replacement?
Q2 Is there a direct replacement that will fit inot the FT-11 case?
Any thoughts?