marks1080
Electrical
- Oct 10, 2006
- 612
I'm working on an old, crude DCB scheme.... The zone 3 elements are 67, not 21. When I think about it... I start wondering if the 67 is actually more secure than a 21. I would never think of using 67 on a new job. When using a Z3 21 you must coordinate with the remote end Z2 21. I guess if you're using a 67 there's no need for coordination?
Anyway.... was just pondering this for a few moments when working on this ancient scheme... I'm temporarily hooking into a new IED and will use the old PLC gear until I get newer teleprotections installed. So my local terminal new IED will use 21 based Z3 elements to supervise my DCB signal, while the remote end uses 67 for its Z3. Anyone have any comments? Is there a solid reason why 21 is better as the supervising Z3 element vs a directional O/C 67? Or... have i just missed something painfully obvious here?
Anyway.... was just pondering this for a few moments when working on this ancient scheme... I'm temporarily hooking into a new IED and will use the old PLC gear until I get newer teleprotections installed. So my local terminal new IED will use 21 based Z3 elements to supervise my DCB signal, while the remote end uses 67 for its Z3. Anyone have any comments? Is there a solid reason why 21 is better as the supervising Z3 element vs a directional O/C 67? Or... have i just missed something painfully obvious here?