Remember this thread from 2012 having having to do with the Grand Prairie, Texas warehouse fire?
Looking at a possible project where the building height is 45' and storage of aluminum cans to 40' and from what I have heard the storage matches exactly what was in the Grand Prairie warehouse including the slip plastic sheets separating layers of cans.
I remember Scott's presentation (no longer available) where he pointed out the slip plastic ("slip plastic" is a term used by the owner) liquefied into a combustible liquid something not pointed out in the Fire Engineering article.
So everyone knows the design criteria will be coming from the insurance company that is not FM. I wouldn't touch fixing the design criteria with a ten foot pole myself but I am curious as to what it might be given the commodity and heights.
I can't find anything that would fit in NFPA #13 2013 and I can't find it in any special head listings either but I haven't reviewed all of them yet.
Anyone have experience with this?
Looking at a possible project where the building height is 45' and storage of aluminum cans to 40' and from what I have heard the storage matches exactly what was in the Grand Prairie warehouse including the slip plastic sheets separating layers of cans.
I remember Scott's presentation (no longer available) where he pointed out the slip plastic ("slip plastic" is a term used by the owner) liquefied into a combustible liquid something not pointed out in the Fire Engineering article.
So everyone knows the design criteria will be coming from the insurance company that is not FM. I wouldn't touch fixing the design criteria with a ten foot pole myself but I am curious as to what it might be given the commodity and heights.
I can't find anything that would fit in NFPA #13 2013 and I can't find it in any special head listings either but I haven't reviewed all of them yet.
Anyone have experience with this?